Hi,
I have to design engine room ventilation system.The machineries are as follows,
1. 300kW diesel engine
2. 30kw diesel generator
Kindly tel me how to do the calculation for this.
 
Thank you ,
I have taken that in to my design .Using this,It gives 5500m3/hr flow rate. but engine emit 27kW heat to the engine room ,I use q=mc(t1-t2) eqn to find the flow rate .It gives 8000m3/hr flow rate (with the consumed Air). Kindly give me some advice .
 
I have never calculated the heat emitted by the engine. It is assumed that, whatever the value, renewing the air 1 time per minute will cause the temperature not to reach exaggerated values. For outdoor air temperatures between 20-32 degrees, that number of renovations should be sufficient.
 