Northern Lights/Lugger genset

Discussion in 'Electrical Systems' started by Nomad, Oct 30, 2002.

  1. Nomad
    Joined: Feb 2002
    Posts: 462
    Likes: 2, Points: 28, Legacy Rep: 12
    Location: Florida

    Nomad Senior Member

    Does anyone here know how to or where to find infromation on "flashing" a 2002 5.5kw genset??
     
  2. MDV
    Joined: Feb 2002
    Posts: 31
    Likes: 1, Points: 0, Legacy Rep: 60
    Location: Singapore

    MDV Junior Member

    If you mean 'Flashing' the exciter due to not being able to get any voltage, then my experience is that 6-8V DC is normally used.
     
  3. Nomad
    Joined: Feb 2002
    Posts: 462
    Likes: 2, Points: 28, Legacy Rep: 12
    Location: Florida

    Nomad Senior Member

    Yes that is what I am talking about. I know you need 2 12 volt batteries but I do not know which wires to hook the up to.
     
  4. MDV
    Joined: Feb 2002
    Posts: 31
    Likes: 1, Points: 0, Legacy Rep: 60
    Location: Singapore

    MDV Junior Member

    I quote from a manual for an ABB 2745kVa Alternator.

    "with the prime mover at rest, apply dc source (non grounded) of not more than 12vDc to terminals F+ (positive) and F- (negative) while observing polarity, in series with a limiting resistor of 23-30 ohms"

    For this application, the F+ & F- terminals are as far as I can see dedicated points for this purpose, and are located on the Voltage Regulator.

    This is the extent of my knowledge on this subject. Hope it helps.


    Michael
     

  5. Nomad
    Joined: Feb 2002
    Posts: 462
    Likes: 2, Points: 28, Legacy Rep: 12
    Location: Florida

    Nomad Senior Member

    Thanks
     