fallguy, I got a response from Sungoldpower saying; “When the inverter is turned off, the inverter is in a power-off state, and the 120V shore power grid is not connected to the inverter output”. Thus, wiring a ByPass circuit as reflected in the diagram I last sent you yesterday would not have a functioning ground connection. Based on that, I redesigned the wiring diagram (attached-Highlighted in Yellow) adding an “all three wires” circuit through an “Always OFF” switch between my ELCB input and my CFCI input terminals. Will this work to serve as a ByPass circuit from the Shore/grid receptacle and the boat’s 120v AC LOAD circuits so I can maintain my 12v Wet HOUSE & starting batteries (using a 12v AC Maintainer) and 120v AC refrigerator when the Solar Panels, Inverter, and Lithium battery are disconnected at their individual circuit breakers?
I also, per your advice, removed the connecting wire between the Earth Ground Bus Bar and the negative terminal on the HOUSE battery.
Do you see any problems wiring the entire solar system as shown or the proposed ByPass circuit? As always, Thanks. Jim