I have purchased a 2000W (2kVA ?) isolation transformer that can be jumpered for 220v or 115v input that I think will meet my needs for lighting, battery charging, etc.
I plan to put a 15A breaker and a GFCI on the output of the transformer but on the input side it would need either 15A (115v shore power) or 8A (220v shore power) breaker to avoid exceeding the transformer rating.
I can think of any number of ways to arrange for the input breaker amperage to differ depending on input voltage and methods to choose between them, but is there a prefered way to implement this ?
Maybe a 220v shore power cable adaptor pigtail with a breaker in it, or some switching arrangement. I'd prefer not to run more cables than necessary inside the boat (it's a longer way than I would like from the shore power inlet to the panel) or to swap out breakers but I suppose it's not a frequent task so that may work. I even considered putting two 8A breakers in parallel and just turning one off when on 220 but I read online this is frowned upon. Or putting an 8A and a 15A in parallel and just leaving one or the other turned off. I'd prefer something "forgetfulnessproof" though but the transformer needs to be re-jumpered anyway so I can't eliminate everything.
Also, I was unable to find a dual pole 8A circuit breaker, can I simply use two 8A single pole breakers and mechanically link the switch levers with a nylon screw and nuts to achieve the same effect or do the dual pole breakers differ internally from two separate single pole ?
I plan to put a 15A breaker and a GFCI on the output of the transformer but on the input side it would need either 15A (115v shore power) or 8A (220v shore power) breaker to avoid exceeding the transformer rating.
I can think of any number of ways to arrange for the input breaker amperage to differ depending on input voltage and methods to choose between them, but is there a prefered way to implement this ?
Maybe a 220v shore power cable adaptor pigtail with a breaker in it, or some switching arrangement. I'd prefer not to run more cables than necessary inside the boat (it's a longer way than I would like from the shore power inlet to the panel) or to swap out breakers but I suppose it's not a frequent task so that may work. I even considered putting two 8A breakers in parallel and just turning one off when on 220 but I read online this is frowned upon. Or putting an 8A and a 15A in parallel and just leaving one or the other turned off. I'd prefer something "forgetfulnessproof" though but the transformer needs to be re-jumpered anyway so I can't eliminate everything.
Also, I was unable to find a dual pole 8A circuit breaker, can I simply use two 8A single pole breakers and mechanically link the switch levers with a nylon screw and nuts to achieve the same effect or do the dual pole breakers differ internally from two separate single pole ?