120 VAC mystery

I just joined up, initially to ask this question though I'm hoping to think of something else to contribute.
Q: A customer of mine (at a marina in the US) recently had a meltdown at his AC neutral connection strip, 120 VAC 30A, because he overloaded his panel with electric heaters and none of the breakers tripped (23 year old trawler, Taiwan built). The mystery for me was that the outlets affected by melted wire tested as having swapped their hot and ground (green safety wire). But half the outlets were okay, even though there's only one breaker for all of them. As I disassembled the neutral strip, the outlets went to a simple open neutral condition, as one would expect. When the strip was replaced and damaged wire ends repaired, conditions returned to normal at all outlets. At no time did the panel ground strip show voltage, nor was current flowing (i.e., a short) that the meter could detect. Methinks there may be other damage, but I cannot find any, nor does the customer want me to begin tearing his conduits apart. Is there any way the positive and grounds can swap, other than from damaged or incorrect wiring? And why would half of the outlets remain unaffected, even when all their grounds were ganged at the same strip? Sorry for all the questions; I'm still scratching my head over this one. Either I was fooled, or my tester was, or both of us.
Reply With Quote
  #2  
Old 03-27-2009, 11:01 AM
jehardiman jehardiman is offline
Senior Member
 
Join Date: Aug 2004
Rep: 1623 Posts: 1,483
Location: Port Orchard, Washington, USA
Is the vessel consistantly wired Y or Delta? Were the effected outlets split between shorepower and ships service? New and original?
__________________
A vessel is nothing but a bunch of opinions and compromises held together by the faith of the builders and engineers that they did it correctly. Therefor the only thing a Naval Architect has to sell is his opinion.
Reply With Quote
  #3  
Old 03-27-2009, 11:07 AM
Boston's Avatar
Boston Boston is offline
Senior Member
 
Join Date: Jul 2008
Rep: 1360 Posts: 3,257
Location: Denver Co
the issue could have been in an appliance that shorted out and fed current to the ground system
ask the customer if there are any appliances that no longer work since the event
Reply With Quote
  #4  
Old 03-27-2009, 12:25 PM
StewartG StewartG is offline
 
Join Date: Mar 2009
Rep: 10 Posts: 4
Location: S.F. Bay Area
I guess it's wired Y--I'm only just learning about Y and Delta wiring. Power comes to the boat in the normal fashion, a shorepower cord, passes to a selector switch for Generator or House, then to a main breaker the ship's service panel, and from there to branch circuit legs. Both the neutral and safety wires are ganged at strips a foot or so away from the circuit breakers. All outlets are original, with no GFCI protection. As far as I know, no appliances failed when the meltdown occurred. While there is evidence of marginal DIY work here and there, the original wiring is not too bad. I couldn't find any evidence of either a ground or line fault, though there is much wiring I couldn't inspect. It looked like a simple overload/meltdown. I never tested the ground/hot swap for its load-carrying ability, was afraid I'd cause another meltdown. And as curious as I am about the cause, the customer is out of $$ and it's a Pandora's Box of liabilities I'm hoping not to open again.
Reply With Quote
  #5  
Old 03-27-2009, 03:21 PM
Boston's Avatar
Boston Boston is offline
Senior Member
 
Join Date: Jul 2008
Rep: 1360 Posts: 3,257
Location: Denver Co
well I got home wiring down to an art but I suspect your systems aboard ship are far more complex than that
so rather than steer you wrong Im just going to read along
best
B

guy named Rick W. in here somewhere seems pretty good with electronics
might try and find him
B
Reply With Quote
  #6  
Old 03-28-2009, 12:38 PM
alan white's Avatar
alan white alan white is offline
Senior Member
 
Join Date: Mar 2007
Rep: 1168 Posts: 3,269
Location: maine
The odd thing is the meltdown occurring at the neutral strip. It sounds more like a short circuit, where a hot wire contacted the strip. If the hot wire involved was overloaded but the breaker failed to operate, it would have possibly melted that hot wire's insulation near the connection to the breaker, allowing the bare copper to contact the neutral strip.

As far as swapping hot for ground on some of the outlets, you don't mention neutral, but obviously if the hot and (green) ground were reversed, nothing plugged into those outlets would ever have worked, since neutral and ground are both grounds. If the neutral and the hot were reversed the outlets involved would have worked fine, with polarity reversed. A recent thread discussed this, where such a condition on a boat would be very dangerous because of proximity to water.
Are GFIs involved, by the way?
Reply With Quote
  #7  
Old 03-31-2009, 04:51 AM
Jack Daniels Eq's Avatar
Jack Daniels Eq Jack Daniels Eq is offline
Shockwave
 
Join Date: Aug 2008
Rep: 11 Posts: 50
Location: Phuket
My nickel is manifold -
You appear to be unqualified to do any troubleshooting, even less repair work
The boat sounds like a typical Rube Goldberg Framus - garage sale components
Anything you do will be wrong & might even contribute to, plus liability looms
Anyone could have swapped leads. cord, polarity anytime - nobody would know or confess for fear of liability to existing marina, boats wiring.
Walk away ...... he clearly has no money either
BR>Jack
Reply With Quote
  #8  
Old 03-31-2009, 06:53 AM
FAST FRED FAST FRED is offline
Senior Member
 
Join Date: Oct 2002
Rep: 700 Posts: 3,208
Location: Conn in summers , Ortona FL in winter , with big dock & room for O'nite stop .
A frequent problem is the white (neutral) and green (ground) are joined somewhere inside the boat,

They can ONLY be joined at the source , so joined at the gen set or inverter is fine , but on board from the dock wiring is not.

Take a look at the selector between the shore , inverter and noisemaker and see what you have.

Its not as "Yachty" but we use plugs and sockets to transfer loads , no fires yet, or burnouts from a bad dock setup.

FF
Reply With Quote
  #9  
Old 03-31-2009, 07:27 AM
Jack Daniels Eq's Avatar
Jack Daniels Eq Jack Daniels Eq is offline
Shockwave
 
Join Date: Aug 2008
Rep: 11 Posts: 50
Location: Phuket
This post get scarier by the mo .....
Please cease & desist
BR>Jack
Reply With Quote
  #10  
Old 03-31-2009, 11:43 AM
Boston's Avatar
Boston Boston is offline
Senior Member
 
Join Date: Jul 2008
Rep: 1360 Posts: 3,257
Location: Denver Co
in my biz electrical issues cause the most fires and although Ive done more than my share of elec work Ild have to second Mr Daniels previous
you staring at a can of worms that could explode at any moment
and on your dime
part of being a good business man is knowing when to walk away

best
B
Reply With Quote
  #11  
Old 04-05-2009, 10:34 AM
StewartG StewartG is offline
 
Join Date: Mar 2009
Rep: 10 Posts: 4
Location: S.F. Bay Area
Thanks all, for your comments, even Jack Daniels' rather backhanded attempts. The mystery will have to remain due to reasons mentioned in my first post. But to answer some of your queries, no, there were no GFCIs involved, and as much as I had to time to search, no other damage or incorrect wiring to be seen. And so there must be either a hidden connection somewhere, or damaged wires unseen. I've run across older Taiwan boats where hidden sub panels were added by the manufacturer that were unprotected by any breaker or fuse at all. This is one of those boats where the only intelligent solution is a complete rewire.
Reply With Quote
Reply



Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes


Similar Threads
Thread Thread Starter Forum Replies Last Post
120 mercruser to 4.3L OMC flounder Inboards 0 09-11-2007 11:39 PM
Impeller for a sport jet 120 Blakeping Jet Drives 0 07-19-2007 08:11 AM
Vac pumps Adam_melb Fiberglass and Composite Boat Building 8 10-05-2006 04:22 AM
vac İnfusions rtreth6307 Fiberglass and Composite Boat Building 1 04-01-2006 02:02 AM
Mercruiser 120 Replacement penguin Propulsion 1 04-23-2005 11:03 PM


All times are GMT -5. The time now is 09:46 AM.


Powered by: vBulletin Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Web Site Design and Content Copyright ©1999 - 2012 Boat Design Net