#1
| ||||
| ||||
| Hi Amp Interupt Capacity Circuit Breakers I am having trouble finding a supplier of hi amperage (7,000 - 10,000 Amp) Interupt capacity circuit breakers... any suggestions...?
__________________ Will Imaginocean Yacht Design Logic will get you from A to B... Imaginocean will take you everywhere else... www.imaginocean.net |
|
#2
| |||
| |||
| Copper bus bar and an Ax, standard for the last 100 years. Really, that looks way too high. There may be some auto control breaker switches out there like on some old DC MPU systems, but just the sheer size of the thing works against you. Probably going to have to go to those who service the power industry, Westinghouse, GE, etc. for a bid. http://www.levydev.com/homewood/PDFs...t-Breakers.pdf
__________________ A vessel is nothing but a bunch of opinions and compromises held together by the faith of the builders and engineers that they did it correctly. Therefor the only thing a Naval Architect has to sell is his opinion. |
|
#3
| ||||
| ||||
| I'm not looking for a 7000 Amp breaker, but a breaker with a 7000 Amp interupt capacity. The breaker(s) might only have trip capacities of 10 or 20 amps. It is for an installation in a 65ft pleasure boat that has a rather large house bank.
__________________ Will Imaginocean Yacht Design Logic will get you from A to B... Imaginocean will take you everywhere else... www.imaginocean.net |
|
#4
| |||
| |||
| Fuse? Disclaimer: I'm not an electrical engineer. Put a fuse with a sufficent interupt capacity and nominal rating ahead of the breakers?
__________________ David Cockey Last edited by DCockey : 11-21-2011 at 10:19 AM. Reason: eliminated incorrect qualifier |
|
#5
| ||||
| ||||
| ANL, 6000, or T class, 20000, fuses feeding the board then just normal breakers
__________________ The boat http://diy-yachts.com/forum/viewtopic.php?f=23&t=239 |
|
#6
| ||||
| ||||
| Quote:
If the breaker trips at 20 Amps, when will it carry 7000 Amps ? Do you mean to say that you need ultra-slow breakers that can handle a 7000 Amps short spike but trip at a sustained 20 Amps ? Usually, if you cannot find the product you need on a planet with 7 billion people, sooner or later you will discover that you do not really need it.
__________________ Stupidity must be a virtue, whole industries, governments, even economies depend on it...... |
|
#7
| ||||
| ||||
| Quote:
Mike
__________________ The boat http://diy-yachts.com/forum/viewtopic.php?f=23&t=239 |
|
#8
| |||
| |||
| MOSFET & current sensing circuit? Tim B.
__________________ Open Source Marine Charting - openpilot.sourceforge.net Open Source Vessel Dynamics opendynamics.engineering.selfip.org |
|
#9
| |||
| |||
| I use Merlin Gerin in part of the world and I think most others do too. Provided through Schieder electric. Normally for DC breakers I go for a c60-hc which gives 10000amps but the do special c32h-dc for DC circuits that I've never used. Most Classifications will still want to see some fuses in the battery and distributed buses. Hope this is what you where looking for. |
|
#10
| ||||
| ||||
| It would require a giant 24 V battery and .0035 ohms circuit resistance to create 7000 Amps. Even if the wiring was AWG #1 solid gold, the terminals and internal resistance of any 20 Amps circuit breaker prohibit such a current to flow. If there exist regulations dictating such current breaking capacities they were written by incompetent people and should be ignored. In any serious power circuit there must be a fuse or fusible link in close proximity to the power source, rated at or slightly above the maximum total current to be allowed through the circuit. It is good practice to use multiple circuits, each with their own fuse, if the total current reaches impractical values.
__________________ Stupidity must be a virtue, whole industries, governments, even economies depend on it...... |
|
#11
| ||||
| ||||
| maybe nuts but thats the regs 1,000 A/h 12V battery 6,000 AIC. Most of the boat books such as Calder's have a little section about it. I am using some ANL's just to have have no arguements if **** ever hits the fan and they are cheap so why not. 600 A/H of lifepo will easily deliver 6,000 into a short , but yes it would sure need a low impedence circuit.
__________________ The boat http://diy-yachts.com/forum/viewtopic.php?f=23&t=239 |
|
#12
| |||
| |||
| The use of too many fuses (ANL's) can lead to a cluttered and bulky distribution. On extreme over current some breakers may weld together, others obliterate themselves if not specified correctly. The price of breakers is not that high and reliability is good if selected correctly. They also make a really tidy job especially when used with tie/bus bars. DC 2-pole tie bars are great for a more professional job of isolating both positive and negative supplies to a consumer. |
|
#13
| ||||
| ||||
| Thanks... will check out the Merlin Gerin.... That it is an unlikely occurance doesn't mean that it can't or doesn't happen. I draw your attention to a recent article by Steve D'Antonio in the October / November issue of Proffesional Boatbuilder where he discusses this very subject. The 12v battery bank in question here has a 1400 AH capacity. T fuses are an option, and that is likely the way we'll go, but I was just looking into the feasibility of putting in a breaker as an option....
__________________ Will Imaginocean Yacht Design Logic will get you from A to B... Imaginocean will take you everywhere else... www.imaginocean.net |
|
#14
| |||
| |||
| theres no problem getting 10000 amp interrupt. Most of CarlingSwitch standard circuit breakers have upto 100amp capacity, and 10000amp interrupt at 80v Dave |
|
#15
| |||
| |||
| If you are seriously worried about a short in the bank, and you have a large (10 or more cells) battery bank, you might consider an automatic battery cell monitoring system which will also help with charging. Combined with a auto cutout system based on the monitoring data, that is pretty standard for large battery installations.
__________________ A vessel is nothing but a bunch of opinions and compromises held together by the faith of the builders and engineers that they did it correctly. Therefor the only thing a Naval Architect has to sell is his opinion. |
![]() |
| Thread Tools | Search this Thread |
| Display Modes | |
| |
Similar Threads | ||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| DC circuit in aluminium boats | Mat-C | OnBoard Electronics & Controls | 5 | 09-13-2011 12:58 AM |
| Simplest possible circuit needed please | L'eau.Life | OnBoard Electronics & Controls | 6 | 02-08-2010 02:36 AM |
| Mooring Force & Winch Capacity calculation | ociship | Boat Design | 4 | 12-07-2009 07:03 PM |
| Circuit Design Software | dfmoss | OnBoard Electronics & Controls | 7 | 06-18-2008 01:38 PM |
| Short circuit | mikep | Electrical Systems | 1 | 03-27-2007 09:15 AM |