Quote:
Originally Posted by Lt. Kludge View Post
Actually I would suggest two contactors. One to connect to either Shore or Onboard and the Other to switch between Inverter and Generator. In-case of contact Weld you will still be interlocked to only one source of supply.
Hi Lt. Kludge, If you had a similar design like CDK, my apology for arguing with you. I misunderstood you, I thought you suggested two contactors with a rotating switch instead of just 2 contactors.
Reply With Quote
  #32  
Old 08-03-2012, 08:32 AM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
CDK got a nice bright idea with this.
Automatic switching of hot and neutrals depending on what is plugged in etc.

One improvement for me would be having a toggle on the grid (shore) power coil. So would not have to unplug heavy power cord from grid power to run gen power, just turn off the relay coil.

Boat is twin 30 amp power and I can easily find 30 amp DPDT relays like this
Coil needs to be 120 V AC



http://www.frys.com/product/1667853
anyone have a link to something cheaper price and or higher amps?

I already use a DPDT relay like this I bought at Radio shack to switch hot-neutrals for the charger-converter. Plug into shore power it is on, unplug and it will use the gen. Makes it very easy.
Reply With Quote
  #33  
Old 08-03-2012, 08:53 AM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
It does get more complex.
I have twin 30 amp shore power cables.
2 hots and 2 neutrals, hots are on different phases. It is like having 240V AC with 2 hots on different phases and a single neutral and boats have done this standard for decades.

I have one generator hot and neutral at 6500 watts ~ 50 amps
I have one invertor hot and neutral at 3000 watts ~ 30 amps

So I think I must have more DPDT relays such as 4 for the grid (shore power) switching of hots and neutrals.
Reply With Quote
  #34  
Old 08-03-2012, 09:41 AM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
110 V AC coil
switches 30 amps at 250V AC
Silver alloy contacts.
push on connectors

question is would this be trustworthy to switch a full 30 amps, price is good

http://www.ebay.com/itm/110VAC-30A-D...ht_1652wt_1028

Reply With Quote
  #35  
Old 08-03-2012, 11:06 AM
Lt. Kludge Lt. Kludge is offline
Junior Member
 
Join Date: Jul 2010
Rep: 23 Posts: 17
Location: Massachusetts, USA
Quote:
Originally Posted by sdowney717 View Post
110 V AC coil
switches 30 amps at 250V AC
Silver alloy contacts.
push on connectors

question is would this be trustworthy to switch a full 30 amps, price is good
Manufacturer - Unknown
Third Party Surveillance - none?

Connectors 0.250 in. Faston tabs, which are rated for 15A?, on a 30A relay?
Reply With Quote
  #36  
Old 08-03-2012, 11:23 AM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
yeah, kinda not great. I have seen some USA type relays rated for 30 amp HVAC use with push on connections.

here is one rated at 30 amps with push on connectors.
Do you think the rating is wrong?
http://www.spadepot.com/shop/Relay-D...P8363C233.aspx

better name?
http://www.amazon.com/Potter-Brumfie...T+relay+120VAC

Cheap Packard Relay, I called them to ask what the amp rating is.
http://www.amazon.com/Packard-PR341-...T+relay+120VAC

Perhaps the Packard is similar to this.
What do they mean when they say
Number of Contacts 2, Contact Amp Rating 30 R, Contact Amp Rating 15 L, Contact Material Silver Alloy??
http://www.amazon.com/Dayton-1EJG7-R...T+relay+120VAC

A poor review by a buyer!
Quote:
This review is from: Dayton 1EJG7 Relay, Power, DPDT, 120VAC, Coil Volts
Title is misleading, the NO rating is 30A, but the NC contacts are only rated for 3 Amps. Either need a disclaimer, or need picture showing side with writing on it.
Reply With Quote
  #37  
Old 08-03-2012, 11:58 AM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
Some relays have 30 amp rating for NO, and only 3 amp for NC
The datasheet shows this
http://documents.tycoelectronics.com...2_T92_0910.pdf

One of these here
http://www.digikey.com/product-detai...B597-ND/678230
Reply With Quote
  #38  
Old 08-03-2012, 12:20 PM
CDK's Avatar
CDK CDK is offline
retired engineer
 
Join Date: Aug 2007
Rep: 1653 Posts: 2,675
Location: Adriatic sea
No sdowney717, I meant serious relays, not toys. For this application you need something you need never worry about anymore.
Attached Thumbnails
create a shore-gen-invertor-off switch using solid state parts-g7z_fe2.jpg  
__________________
cogito, ergo sum (Descartes' credo)
Reply With Quote
  #39  
Old 08-03-2012, 09:24 PM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
Do you have a link to the part ?
I can see what will happen is, the prices of all the relays will approach just buying a manual switch.
Reply With Quote
  #40  
Old 08-04-2012, 04:10 AM
CDK's Avatar
CDK CDK is offline
retired engineer
 
Join Date: Aug 2007
Rep: 1653 Posts: 2,675
Location: Adriatic sea
This is where the picture came from: http://www.ia.omron.com/product/fami...index_fea.html

It need not be overly expensive. In the past I purchased several similar items through Ebay between $10 and $20, mostly products from AEG. All feature screw type terminals and a standard footprint for a mounting rail.
__________________
cogito, ergo sum (Descartes' credo)
Reply With Quote
  #41  
Old 08-04-2012, 06:38 AM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
Am I reading the amp ratings properly?
Too low?

Rated carry current
NO 40 A
NC 25 A

Inductive load is 10 on the NC at 480v AC
Are they talking as in running inductive motors?

If the contact is run at 120V AC, does this mean the contact can carry significantly more amperage current?

Also coil voltage is DC 12 or 24.
Seeing 4 poles available, current output from gen could be on the NC side and split across 2 poles hot and 2 poles neutral. So would be better then?

Also only mentions DPST design not DPDT which sort of means it is not going to work? I thought this should be a DPDT design.

Ideally a 4PDT reversing contactor with both sides rated the same amperage and a 120 V AC coil. Then all you need would be two reversing contactors.

Otherwise, it would take more of the relays and a lot more control, it wont work like the diagram you show.
Attached Thumbnails
create a shore-gen-invertor-off switch using solid state parts-relayamps.png  create a shore-gen-invertor-off switch using solid state parts-dpst.png  
Reply With Quote
  #42  
Old 08-04-2012, 07:26 AM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
Here is a 4PDT 35 amp rated open frame relay with 120vAC coil. Continuous duty

Would need 2 to get it done, so up to $160 in price.

http://www.grainger.com/Grainger/STR...&cm_vc=IDPRRZ1



Problem is price keeps climbing yet still cheaper option than Newmar switch.

Quote:
Features Continuous Duty, Reliable wipe action switching, Silver Alloy Contacts, Screw Terminals, plastic and metal enclosure available
Response Time 40 ms
What a mess, who knows what the relay amperage contact really is for this. Reading the TYCO datasheet claims it is 25 AMPS, but many web sites seeling the part says 35 AMPS, so who is correct?? Both, neither, anything goes, amps dont matter, etc....

Different manufacturer lists different ratings, yet similar part number? Is this one made by TYCO, another by Potter Brumsfield, another by Struthers-Dunn?, all with different ratings?

http://www.datasheetarchive.com/PM-1...datasheet.html

Seeing I am dealing with a max of 30 amps, I would still likely use it.

search for PM-17AY-120A lists
https://www.google.com/search?q=PM-1...hrome&ie=UTF-8
Attached Thumbnails
create a shore-gen-invertor-off switch using solid state parts-pmseries4pdtrelay.png  
Reply With Quote
  #43  
Old 08-04-2012, 12:08 PM
sdowney717 sdowney717 is offline
Senior Member
 
Join Date: Nov 2010
Rep: 161 Posts: 282
Location: Newport News VA
I got two of these struthers dunn off ebay for total $40 used relays. Seller sold it as a lot of two. I hope they are the same, the picture he showed looked the same as did the part number.

http://struthersdunn.thomasnet.com/i...c?#Temperature

Should work for this, rated up to 35 amps and price was ok. At some price point it is better to go one way or the other, this was decent.

I plan to do a hookup similar to the original idea. I will put the gen on the default because it has an auto demand start feature that is load sensing.

I will gang up the poles for the gen as it can output 6500 watts, so 2 poles will share the hot load, and 2 poles the neutral load.

Invertor is only 3000 watt so only needs to use one set of switching poles which leaves the others unused or should i just hook them up anyway.

Or perhaps some other useless task can be arranged for them.
Will see how it goes as it gets wired up.

It is better than what I have now, it still likely would not meet some code, regulation, rule, etc... somewhere deep in the bowels of some book a gnome would love.
Reply With Quote
  #44  
Old 08-04-2012, 12:18 PM
CDK's Avatar
CDK CDK is offline
retired engineer
 
Join Date: Aug 2007
Rep: 1653 Posts: 2,675
Location: Adriatic sea
Yes, they look good and have 4 contacts so you can double the current capacity. All you need now is a sturdy plastic box around them and a "danger, do not touch" decal.
__________________
cogito, ergo sum (Descartes' credo)
Reply With Quote
  #45  
Old 08-04-2012, 02:24 PM
BertKu BertKu is offline
Senior Member
 
Join Date: May 2009
Rep: 153 Posts: 1,309
Location: South Africa Little Brak River
Sdowney,
Something to remember about relays and contactors. The manufacturer normally state the maximum current what is allowed to be switched on/off. If a contact is made and you have a decent quality manufacturer, the closed contact current can be higher. Logical not 10 times, but up to 20% is normally allowed.

If the contact use paladium, even a higher percentage. Now my question to you: ARE YOU SWITCHING 6,5 KW ON and OFF or are you starting low and move up in power and also bring the power down and switch off then?

The reason I ask, parallel switching of two contacts , under power should not be double, but double minus 20 %. The reason is that two contacts never closes at the same time, how small the difference may be, for that period, the full double current is on one contact.
Reply With Quote
Reply



Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need help: Mercruiser Alpha Gen II or Bravo II ?? Bruce P Propulsion 4 12-13-2010 01:04 PM
small 130A invertor welders. Frosty Open Discussion: All Things Boats & Boating 15 02-25-2010 04:16 PM
Gen-set for a Pilot-boat. toveri Diesel Engines 4 05-21-2009 12:54 PM
mercruiser alpha one gen 2 won't start steve3211 Sterndrives 4 04-04-2008 03:30 AM
Solid Works V Solid Edge alidesigner Software 11 11-26-2006 10:08 PM


All times are GMT -4. The time now is 09:45 PM.


Powered by: vBulletin Copyright ©2000 - 2013, Jelsoft Enterprises Ltd.
Web Site Design and Content Copyright ©1999 - 2013 Boat Design Net